I have a PFC200 (750-8217, FW 04.07.03(29)) connected to a 765-4501 IO-Link master, programmed in Structural Text using CODESYS 3.5 (SP21, Patch 1). The set-up is designed to accommodate various hardware configurations, and I would like to query whether certain ports on the IO-Link master are configured as DO, DI, or IOL. I have tried to use EtherNetIP Services (ENIP) library (v. 4.5.0.0) to conduct an async query for this. The code I have is provided below, but this returns the error: “PATH\_DESTINATION\_UNKNOWN”. Grateful for any advice to help resolve this issue.

```auto
FUNCTION_BLOCK PUBLIC FbIOLMaster_PortCheck
(*	
	Authors : JV
	Last Edit	: 03 Sep 2026 (JV)	
	Device : PLC

	FB to manage async-communications with IO-Link master to check port configuration
	(Note: if want to async set config, could adapt this code to use the Set_Attribute_Single FB)

	EXECUTION FB - EDGE TRIGGERED
*)
VAR_IN_OUT
	xTrigger : BOOL; // Starts with rising edge on Trigger
END_VAR
VAR_INPUT
	xNewMale : BOOL; // Trigger value of boom
	eNewIOLMaster : EnIOLMaster; // Trigger value of IOLink master type
	usiNewMaster : USINT; // Trigger value of IOLink master index
	usiNewPort : USINT; // Trigger value of IO-Link master physical port number (e.g. 1-8)
END_VAR
VAR_OUTPUT
	oStatus : StFbEdgeStatus; // structure reporting fb status
END_VAR
VAR

	// EIP library variables
	oEIP : ENIP.Get_Attribute_Single;
	xEIPTrigger : BOOL;
	xEIPDone : BOOL;
	xEIPBusy : BOOL;
	xEIPError : BOOL;
	eEIPError : ENIP.ERROR;
	
	itfEIPDevice : ENIP.IEtherNetIPService;
	oEIPClass : ENIP.CIPClass := 16#F4; //	Port Object (possibly 16#0381, 16#F4)
	dwEIPInstance : DWORD;
	wEIPAttribute : WORD;
	byPortMode : BYTE;
	udiEIPReadDataSize	: UDINT;
	
	// local variables
	xInit : BOOL;
	eState : EnIOLMasterComms; // current state of machine
	eIOLMaster : EnIOLMaster; // type of IOLink master
	usiMaster : USINT; // IOLink master index
	xMale : BOOL; // boom
	usiPort : USINT; // IO-Link master physical port number (e.g. 1-8)
	
	tTimeout : TIME := T#30S; // timeout
	oWatchDog : TON;
	oLogEntry : StLogEntry;
END_VAR

IF NOT xTrigger THEN

	
	(* ========================*)
	(* ===== [Set idle] =====*)
	(* ========================*)

	eState := EnIOLMasterComms.Idle;
ELSE

	(* ===============================*)
	(* ===== [Process trigger] =====*)
	(* ===============================*)

	oStatus.xDone := FALSE;
	oStatus.xError := FALSE;
	IF oStatus.xBusy THEN
		// already busy - check if need to abort current task
		
		IF xNewMale <> xMale OR
			eNewIOLMaster <> eIOLMaster OR
			usiNewMaster <> usiMaster OR
			usiNewPort <> usiPort THEN
			// abort existing task

			xInit := TRUE;			
			eState := EnIOLMasterComms.CheckEIPConnection;
			oStatus.sMessage := 'New task started - previous task aborted';
		END_IF
	ELSE
		
		xInit := TRUE;			
		eState := EnIOLMasterComms.CheckEIPConnection;
		oStatus.sMessage := 'New task started';
	END_IF
	IF xInit THEN
		
		xMale := xNewMale;
		eIOLMaster := eNewIOLMaster;
		usiMaster := usiNewMaster;
		usiPort := usiNewPort;
		oStatus.xBusy := TRUE;
		IF xMale AND eIOLMaster = EnIOLMaster.MURR THEN
			
			itfEIPDevice := IOLMMURR1;
		ELSIF xMale AND eIOLMaster = EnIOLMaster.WAGO AND usiMaster = 1 THEN
			
			itfEIPDevice := IOLMWAGO1;
		ELSIF xMale AND eIOLMaster = EnIOLMaster.WAGO AND usiMaster = 2 THEN
			
			itfEIPDevice := IOLMWAGO2;
		ELSIF NOT xMale AND eIOLMaster = EnIOLMaster.MURR THEN
			
			itfEIPDevice := IOLFMURR1;
		ELSIF NOT xMale AND eIOLMaster = EnIOLMaster.WAGO AND usiMaster = 1 THEN
			
			itfEIPDevice := IOLFWAGO1;
		ELSIF NOT xMale AND eIOLMaster = EnIOLMaster.WAGO AND usiMaster = 2 THEN
			
			itfEIPDevice := IOLFWAGO2;
		ELSE
			
			oStatus.xBusy := FALSE;
			oStatus.xDone := FALSE;
			oStatus.xError := TRUE;
			oStatus.sMessage := 'Unrecognised system for IOLMaster_Comms';
			eState := EnIOLMasterComms.Waiting;
		END_IF
		xInit := FALSE;			
	END_IF
END_IF

(* =============================*)
(* ===== [State Machine] =====*)
(* =============================*)

CASE eState OF

	EnIOLMasterComms.Idle:	
		IF oStatus.xBusy THEN
			
			oStatus.sMessage := 'Idle - previous task aborted';
		ELSE
			
			oStatus.sMessage := 'Idle';
		END_IF
		oStatus.xBusy := FALSE;
		oStatus.xDone := FALSE;
		oStatus.xError := FALSE;
	
	EnIOLMasterComms.CheckEIPConnection : 
		IF NOT FnIOL_CheckAdapterRunning(eIOLMaster:=eIOLMaster, usiMaster:=usiMaster, xMale:=xMale) THEN

			oStatus.xBusy := FALSE;
			oStatus.xDone := TRUE;
			oStatus.sMessage := 'IOL master not running';
		ELSE

			eState := EnIOLMasterComms.InitialiseRead;
		END_IF
	

	EnIOLMasterComms.InitialiseRead : 
		xEIPTrigger := TRUE; //	Setting this variable TRUE will execute the EIP function block
		dwEIPInstance := USINT_TO_DWORD(usiPort); //	This is the physical port number (1-8)
		wEIPAttribute := 1; //	1 = Pin 4, 2 = Pin 2
		eState := EnIOLMasterComms.Waiting;
		
	EnIOLMasterComms.Waiting :
		;
END_CASE

(* ===============================*)
(* ===== [Pass to workers] =====*)
(* ===============================*)

oEIP(
	xExecute := xEIPTrigger,
	xDone => xEIPDone,
	xBusy => xEIPBusy,
	xError => xEIPError,
	eError => eEIPError,
	itfEtherNetIPDevice := itfEIPDevice,
	eClass := oEIPClass,
	dwInstance := dwEIPInstance,
	wAttribute := wEIPAttribute,
	pData := ADR(byPortMode),
	udiDataSize := SIZEOF(byPortMode),
	udiReceivedDataSize => udiEIPReadDataSize
);
	
IF xEIPError THEN
	xEIPTrigger := FALSE;	 
	oStatus.xBusy := FALSE;
	oStatus.xError := TRUE;
	oStatus.sMessage := WagoAppString.Concat3('EIP error: ','', TO_STRING(eEIPError));
ELSIF xEIPDone THEN 
	xEIPTrigger := FALSE;	 
	oStatus.xBusy := FALSE;
	oStatus.xDone := TRUE;
	oStatus.sMessage := 'Complete';
END_IF

(* ==============================*)
(* ===== [Watchdog Timer] =====*)
(* ==============================*)

IF oWatchDog.Q AND oStatus.xBusy THEN

	oStatus.xBusy := FALSE;
	oStatus.xError := TRUE;
	oStatus.sMessage := 'Timeout';
END_IF
oWatchDog( IN := oStatus.xBusy, PT := tTimeout);

(* =============================*)
(* ===== [Log reporting] =====*)
(* =============================*)

IF oStatus.xError OR oStatus.xDone THEN
	
	IF oStatus.xError THEN
		
		oLogEntry.udiLogClass := CmpLog.LogClass.LOG_ERROR;
	ELSE
		
		oLogEntry.udiLogClass := CmpLog.LogClass.LOG_INFO;
	END_IF
	IF xMale THEN
		
		oLogEntry.enCallingUnit	:= EnPOUReference.MaleFbIOLMaster_Comms;
	ELSE
		
		oLogEntry.enCallingUnit	:= EnPOUReference.FemaleFbIOLMaster_Comms;
	END_IF
	oLogEntry.sMessage := oStatus.sMessage;
	GvSQL.oSQLProcessing.AddLogEntry(oLogEntry);
END_IF

(* ===============================*)
(* ===== [Update xTrigger] =====*)
(* ===============================*)

xTrigger := oStatus.xBusy;

```

---

<div class="post-metadata">

**Author:** ![MikePsaltis](https://sea2.discourse-cdn.com/flex016/user_avatar/www.wago.community/mikepsaltis/32/47_2.png) [@MikePsaltis](https://www.wago.community/u/MikePsaltis)\
**Post date:** [September 3, 2026, 2:29pm UTC](https://www.wago.community/t/765-4501-port-configuration-query/2864/2 "2026-09-03T14:29:39Z")

</div>

Hi Justin,

Here is a test project I made that an read/write the IOL port configurations. Hope this helps!

[![](https://us1.discourse-cdn.com/flex016/uploads/wago/original/2X/3/322adc863962a2981b2925c765a099b2b0ba3a20.jpeg "WAGO IO Field Config with Explicit EIP Message") ](https://www.youtube.com/watch?v=7zd_pYSUNzc)

[Example - Runtime Port Configuration.project](https://www.wago.community/uploads/short-url/KGfif8YNb47ErIMeVUtkHgCcry.project) (980 KB)