# A complete PLC shutdown due to OPC UA?

**URL:** https://www.wago.community/t/a-complete-plc-shutdown-due-to-opc-ua/2888
**Category:** CODESYS
**Created:** [September 22, 2026, 12:53pm UTC](https://www.wago.community/t/a-complete-plc-shutdown-due-to-opc-ua/2888 "2026-09-22T12:53:57Z")
**Posts on this page:** 3
**Page:** 1

<div class="post-metadata">

### Author: ![TomasD](https://sea2.discourse-cdn.com/flex016/user_avatar/www.wago.community/tomasd/32/2042_2.png) [@TomasD](https://www.wago.community/u/TomasD)
#### Post date: [September 22, 2026, 12:53pm UTC](https://www.wago.community/t/a-complete-plc-shutdown-due-to-opc-ua/2888/1 "2026-09-22T12:53:57Z")

</div>

I’ve run into this problem (not for the first time) where my PLC freezes, and the only thing that helps is a reboot.  
I found the following in the logs:  
runtime.log.1  
Sep 22 09:16:26 localhost codesys3: CmpOPCUAStack DEBUG OpcUa\_TcpListener\_CloseConnection: Error 0x00000000 removing connection 0xb21ef208!  
Sep 22 09:16:26 localhost codesys3: CmpOPCUAServer EXCEPTION Unhandled exception in OPC UA server. Please restart the PLC.  
Sep 22 09:16:26 localhost codesys3: CmpSupervisor DEBUG Description=Exception occured within the OPC UA Server  
Sep 22 09:16:26 localhost codesys3: IoDrvDal DEBUG stops triggering driver-watchdogs; failure info from CmpSupervisor  
Sep 22 09:16:26 localhost codesys3: IoDrvDal DEBUG Component ID=0x00000124 is out of order! Vital operation ID=0x00000001 failed!  
Sep 22 09:16:26 localhost codesys3: IoDrvDal DEBUG Operation description: ‘Exception occured within the OPC UA Server’  
Sep 22 09:38:54 localhost codesys3: IECVisualization DEBUG Visu\_PRG: Creating Client for Extern-ID: 2469809092  
Sep 22 09:38:54 localhost codesys3: IECVisualization DEBUG Visu\_PRG: Creating Client successful for Extern-ID: 2469809092 Returned IEC-ID: 1  
Sep 22 09:51:19 localhost codesys3: IECVisualization DEBUG VisuFctCheckForUnusedClients: Removing Client with IEC-ID: 1  
Time delta: T#45s985ms Locks: Paintbuffer: TRUE  
Sep 22 09:51:19 localhost codesys3: IECVisualization DEBUG VisuFctCheckForUnusedClients: Successfully Removed Client at Address: 2999433664, IEC-ID was: 1, EXT-ID: 2469809092  
Sep 22 09:53:22 localhost codesys3: IECVisualization DEBUG Visu\_PRG: Creating Client for Extern-ID: 975774383  
Sep 22 09:53:22 localhost codesys3: IECVisualization DEBUG Visu\_PRG: Creating Client successful for Extern-ID: 975774383 Returned IEC-ID: 1

Wago Ethernet settings status:  
Error code: 9  
Argument: 5  
Unknown blink code 9 / 5  
More details about this blink code, refer to the manual of the device.

Has anyone else run into this problem? What should I do?  
Maybe I’m looking in the wrong direction? Where should I look if the problem occurs again?

---

<div class="post-metadata">

### Author: ![WagoTorgeir](https://sea2.discourse-cdn.com/flex016/user_avatar/www.wago.community/wagotorgeir/32/78_2.png) [@WagoTorgeir](https://www.wago.community/u/WagoTorgeir)
#### Post date: [September 22, 2026, 1:25pm UTC](https://www.wago.community/t/a-complete-plc-shutdown-due-to-opc-ua/2888/2 "2026-09-22T13:25:57Z")

</div>

Hi Tomas,  
The described symptom resembles one of the problems which has been solved in FW31; what firmware version does your PLC run ?

---

<div class="post-metadata">

### Author: ![TomasD](https://sea2.discourse-cdn.com/flex016/user_avatar/www.wago.community/tomasd/32/2042_2.png) [@TomasD](https://www.wago.community/u/TomasD)
#### Post date: [September 22, 2026, 2:00pm UTC](https://www.wago.community/t/a-complete-plc-shutdown-due-to-opc-ua/2888/3 "2026-09-22T14:00:03Z")

</div>

It’s been working for about a week, and now I’m getting an error.  
PLC 750-8212  
Version 04.09.01(31)