I am using WAGO BACnet Configurator to transfer data from Daikin to the PFC100 so I can monitor and control the ACs through CODESYS WebVisu.
I can change the AC temperature setpoint and start/stop the ACs through WebVisu.
However, I cannot get the Daikin Analog Input (AI) temperature and Digital Input (DI) alarm values to update when mapped directly to PFC100 AI/DI objects in WAGO BACnet Configurator.
As a workaround, I created Analog Value objects for temperatures and Binary Value objects for alarms. These values update correctly in PFC100 in WAGO BACnet Configurator, but when I display them in WebVisu, the values remain stuck and do not update.
I have mapped the daikin tag to an Analog Value in PFC100 in the WAGO BACnet Configurator, and I can see the value updating correctly on the PFC100 in the software. However, the same tag in CODESYS is not updating.
In second image I tried to map daikin Analog Input variable in PFC100 Analog input, but it didn’t work after store and downloading its present value was showing blank.
In third image its showing values in PFC100 I marked in red box you can see it is showing updated value.
Then I synchronized with codesys , in codesys I got the Analog Value tags and added that same tag which was showing values in wago configurator software in graphics see below image but it’s not updating it stuck at the first value.