BACnet Values Not Updating in WebVisu

  • Controller: WAGO PFC100 – 750-8112

  • Firmware: 31

  • BACnet licence: Enabled

  • Daikin DBACS for air conditioners

I am using WAGO BACnet Configurator to transfer data from Daikin to the PFC100 so I can monitor and control the ACs through CODESYS WebVisu.

I can change the AC temperature setpoint and start/stop the ACs through WebVisu.

However, I cannot get the Daikin Analog Input (AI) temperature and Digital Input (DI) alarm values to update when mapped directly to PFC100 AI/DI objects in WAGO BACnet Configurator.

As a workaround, I created Analog Value objects for temperatures and Binary Value objects for alarms. These values update correctly in PFC100 in WAGO BACnet Configurator, but when I display them in WebVisu, the values remain stuck and do not update.

Did you also do the hardware mapping?

No, I have only configured

You must map the WAGO I/O to the Bacnet objects, otherwise nothing will happen.

The configurator can automatically create this during synchronization.

Could you please elaborate on this for me?

I have mapped the daikin tag to an Analog Value in PFC100 in the WAGO BACnet Configurator, and I can see the value updating correctly on the PFC100 in the software. However, the same tag in CODESYS is not updating.

I don’t understand exactly what they did.

Please send screenshots of your current configuration.

In first Image I mapped daikin Analog Input variable to Analog Value after store and downloading it was showing me values.

In second image I tried to map daikin Analog Input variable in PFC100 Analog input, but it didn’t work after store and downloading its present value was showing blank.

In third image its showing values in PFC100 I marked in red box you can see it is showing updated value.

Then I synchronized with codesys , in codesys I got the Analog Value tags and added that same tag which was showing values in wago configurator software in graphics see below image but it’s not updating it stuck at the first value.

You don’t write directly to an AI’s PresentValue; that is only possible if the data point is OutOfService.
(BACnet Standard)

If you are receiving values via communication, please use Analog-Value objects for this purpose.

Why exactly do you want to use an AI object for this?

If you’d like, please send me the project and the WBC file. I’ll replicate it on a WAGO device and then present you with a solution.

Could you please share your email ID so I can send you?