# Edit Request Packet Interval in Enthernet/IP Scanner

**URL:** <https://www.wago.community/t/edit-request-packet-interval-in-enthernet-ip-scanner/2941>\
**Category:** CODESYS\
**Created:** [November 6, 2026, 9:02pm UTC](https://www.wago.community/t/edit-request-packet-interval-in-enthernet-ip-scanner/2941 "2026-11-06T21:02:25Z")\
**Posts on this page:** 4\
**Page:** 1

<div class="post-metadata">

**Author:** ![coleman.collins](https://avatars.discourse-cdn.com/v4/letter/c/9fc29f/32.png) [@coleman.collins](https://www.wago.community/u/coleman.collins)\
**Post date:** [November 6, 2026, 9:02pm UTC](https://www.wago.community/t/edit-request-packet-interval-in-enthernet-ip-scanner/2941/1 "2026-11-06T21:02:26Z")

</div>

I’ve got a wago 750-8212/000-100 PFC200 BACnet controller running on codesys 3.5 sp 18 patch 4+. The plc is communicating with allen bradley devices (powerflex 753, smc flex, e300) via ethernet ip using the ethernet/ip scanner. I’m trying to change the request packet interval for some of these enet/ip devices.

 ![image](https://us1.discourse-cdn.com/flex016/uploads/wago/original/2X/e/e9fd96d4f0bd1ae1777bc6866c68f1a03e31fabf.png)

I’m not able to change this. I’ve tried changing it online in both run and stop mode. I’ve tried changing it offline while in run mode and in stop mode. I’ve done a clean and clean all and still can’t change this value. I’ve also tried finding the tag and writing to it in structured text but I can’t browse to this tag value anywhere. The value is grey which seems to be read only but I see the current value is different than the default value so I know it’s been changed. How do I change this?

---

<div class="post-metadata">

**Author:** ![AdamReeve](https://sea2.discourse-cdn.com/flex016/user_avatar/www.wago.community/adamreeve/32/59_2.png) [@AdamReeve](https://www.wago.community/u/AdamReeve)\
**Post date:** [November 10, 2026, 2:26pm UTC](https://www.wago.community/t/edit-request-packet-interval-in-enthernet-ip-scanner/2941/2 "2026-11-10T14:26:36Z")

</div>

I’m wondering why your Generic EIP Device tab doesn’t show General, Connection, and Assemblies tabs. Did those simply get cropped out of your screenshot? The RPI is typically specified when creating the Connection to the device.

The oldest CODESYS version I have installed that I can check is SP19 Patch 7, but I don’t remember any significant changes here. But I could be wrong, maybe SP18 handled it differently.

 ![image](https://us1.discourse-cdn.com/flex016/uploads/wago/original/2X/e/ed9eee036bb328e250c15e444c80c29cb536b086.png)  
(image taken with CS3.5.19.7)

---

<div class="post-metadata">

**Author:** ![coleman.collins](https://avatars.discourse-cdn.com/v4/letter/c/9fc29f/32.png) [@coleman.collins](https://www.wago.community/u/coleman.collins)\
**Post date:** [November 10, 2026, 3:38pm UTC](https://www.wago.community/t/edit-request-packet-interval-in-enthernet-ip-scanner/2941/3 "2026-11-10T15:38:01Z")

</div>

Here’s a full screenshot of a new device connection I’ve added in my 3. sp 18 project:

 ![image](https://us1.discourse-cdn.com/flex016/uploads/wago/original/2X/2/231d99695396d52817c36497edc53ed8d9ee8d6d.png)

I do not have all the tabs that you have in your picture.

---

<div class="post-metadata">

**Author:** ![AdamReeve](https://sea2.discourse-cdn.com/flex016/user_avatar/www.wago.community/adamreeve/32/59_2.png) [@AdamReeve](https://www.wago.community/u/AdamReeve)\
**Post date:** [November 10, 2026, 4:36pm UTC](https://www.wago.community/t/edit-request-packet-interval-in-enthernet-ip-scanner/2941/4 "2026-11-10T16:36:45Z")

</div>

Something might have broken in your CODESYS installation. I’m not sure how you could even define your EIP device connections (Assembly Objects, Assembly Object sizes, etc) without those tabs.

I just opened an old VM that has version 3.5.18.5 installed, and I see screens that match my screenshot above, not yours, so I don’t think there were major changes. The devices I added to my project were:  
Ethernet 4.2.0.0  
Ethernet/IP Scanner 4.5.1.0 (both WAGO and 3S versions looked the exact same)  
Generic Ethernet/IP Device 4.1.0.0

If possible, you may want to consider updating your PLC to newer firmware (FW31 is latest) and install CODESYS 3.5.21.7 to start fresh. It shouldn’t be hard to import your existing program, you’ll just have to install the new WAGO Device Description package and the update all your Library Manager placeholders.