# Modbus TCP issues on Power Cycle

**URL:** https://www.wago.community/t/modbus-tcp-issues-on-power-cycle/1124
**Category:** CODESYS
**Created:** [August 8, 2024, 10:07pm UTC](https://www.wago.community/t/modbus-tcp-issues-on-power-cycle/1124 "2024-08-08T22:07:15Z")
**Posts on this page:** 3
**Page:** 1

<div class="post-metadata">

### Author: ![durallymax](https://avatars.discourse-cdn.com/v4/letter/d/9fc348/32.png) [@durallymax](https://www.wago.community/u/durallymax)
#### Post date: [August 8, 2024, 10:07pm UTC](https://www.wago.community/t/modbus-tcp-issues-on-power-cycle/1124/1 "2024-08-08T22:07:15Z")

</div>

Using a 750-8000 (believe I have experienced this with 750-8212 as well) with several Schneider ATV630 VFDs as Modbus slaves using their built in Modbus TCP. When a drive is power cycled, I watch the triangle with exclamation point show up in the tree and connection is never re-established until the PLC itself is power-cycled. Is there a way to reset this connection while running or am I missing something in the handling/setup of these devices?

---

<div class="post-metadata">

### Author: ![TomasD](https://sea2.discourse-cdn.com/flex016/user_avatar/www.wago.community/tomasd/32/2042_2.png) [@TomasD](https://www.wago.community/u/TomasD)
#### Post date: [August 9, 2024, 11:38am UTC](https://www.wago.community/t/modbus-tcp-issues-on-power-cycle/1124/2 "2024-08-09T11:38:43Z")

</div>

There is a way, you need to check the box in the auto-connection settings.

---

<div class="post-metadata">

### Author: ![durallymax](https://avatars.discourse-cdn.com/v4/letter/d/9fc348/32.png) [@durallymax](https://www.wago.community/u/durallymax)
#### Post date: [August 9, 2024, 2:26pm UTC](https://www.wago.community/t/modbus-tcp-issues-on-power-cycle/1124/3 "2024-08-09T14:26:40Z")

</div>

Found it, thank you!