# PFC 200, 750-8212 unable to connect via Ethernet to laptop (first time setup)

**URL:** <https://www.wago.community/t/pfc-200-750-8212-unable-to-connect-via-ethernet-to-laptop-first-time-setup/1690>\
**Category:** Hardware and Linux\
**Tags:** pfc200, how-to\
**Created:** [March 22, 2025, 10:36am UTC](https://www.wago.community/t/pfc-200-750-8212-unable-to-connect-via-ethernet-to-laptop-first-time-setup/1690 "2025-03-22T10:36:48Z")\
**Posts on this page:** 10\
**Page:** 1

<div class="post-metadata">

**Author:** ![Beker](https://avatars.discourse-cdn.com/v4/letter/b/f475e1/32.png) [@Beker](https://www.wago.community/u/Beker)\
**Post date:** [March 22, 2025, 10:36am UTC](https://www.wago.community/t/pfc-200-750-8212-unable-to-connect-via-ethernet-to-laptop-first-time-setup/1690/1 "2025-03-22T10:36:48Z")

</div>

Good morining, I bought new PLC last week and i can’t conect with it. It seams to me that my pc doesn’t see that i connected the plc. I downloaded wago ethernet setting but it also can’t seem to find the plc. The plc itself shows that everytching is connected in the matter of ethernet conection. So my question stands what do I do now. I thougt about just buying the wago comunication cable but it is the last measure for me. I dont undrestand why my pc doesnt see it at all. If it changes sometching, the “Run” LED lights red up, but I think it should because the PLC has no program. Another thing is that the I/0 blinks in a sequence of 4-8, but it has to do with my inputs, because one of them is probably inactive.

---

<div class="post-metadata">

**Author:** ![JohnDitter](https://sea2.discourse-cdn.com/flex016/user_avatar/www.wago.community/johnditter/32/68_2.png) [@JohnDitter](https://www.wago.community/u/JohnDitter)\
**Post date:** [March 22, 2025, 3:29pm UTC](https://www.wago.community/t/pfc-200-750-8212-unable-to-connect-via-ethernet-to-laptop-first-time-setup/1690/2 "2025-03-22T15:29:37Z")

</div>

Error code 4-8 indicates an interruption in the internal bus after the 8th module. Do you have an End Module (750-600) at the end of the node? This is required.

 ![image](https://us1.discourse-cdn.com/flex016/uploads/wago/original/2X/a/a40d404dd0ca029cd8c6af6fb0fcef5ad66fe014.png)

---

<div class="post-metadata">

**Author:** ![Beker](https://avatars.discourse-cdn.com/v4/letter/b/f475e1/32.png) [@Beker](https://www.wago.community/u/Beker)\
**Post date:** [March 22, 2025, 3:59pm UTC](https://www.wago.community/t/pfc-200-750-8212-unable-to-connect-via-ethernet-to-laptop-first-time-setup/1690/3 "2025-03-22T15:59:23Z")

</div>

No i do not have one. Do you think that this may cause all the issues with connecting plc to my computer?

---

<div class="post-metadata">

**Author:** ![JohnDitter](https://sea2.discourse-cdn.com/flex016/user_avatar/www.wago.community/johnditter/32/68_2.png) [@JohnDitter](https://www.wago.community/u/JohnDitter)\
**Post date:** [March 22, 2025, 5:04pm UTC](https://www.wago.community/t/pfc-200-750-8212-unable-to-connect-via-ethernet-to-laptop-first-time-setup/1690/4 "2025-03-22T17:04:30Z")

</div>

Did you assign an IP address to the PFC? It needs to be on the same subnet as your laptop.

You can temporarily assign the IP address 192.168.1.17 to the PFC by setting the mode switch to STOP and holding down the RST push button for more than 8 seconds.

The SYS LED will flash orange when the temporary assignment is in effect.

You can then access the PFC’s built-in web pages using a web browser with the temporary IP address (username: admin, password: wago) and assign it a static IP

---

<div class="post-metadata">

**Author:** ![Beker](https://avatars.discourse-cdn.com/v4/letter/b/f475e1/32.png) [@Beker](https://www.wago.community/u/Beker)\
**Post date:** [March 23, 2025, 7:23am UTC](https://www.wago.community/t/pfc-200-750-8212-unable-to-connect-via-ethernet-to-laptop-first-time-setup/1690/5 "2025-03-23T07:23:12Z")

</div>

Yes i tryed rst but the ip in the configuration doesn’t change. When i try to go to the web side it show me this site is unreachable.

---

<div class="post-metadata">

**Author:** ![antauva](https://avatars.discourse-cdn.com/v4/letter/a/4bbf92/32.png) [@antauva](https://www.wago.community/u/antauva)\
**Post date:** [March 24, 2025, 10:08am UTC](https://www.wago.community/t/pfc-200-750-8212-unable-to-connect-via-ethernet-to-laptop-first-time-setup/1690/6 "2025-03-24T10:08:45Z")

</div>

> [@JohnDitter](#):
>
> 192.168.1.17

> [@How To: Connecting a PFC100/PFC200 to the Internet](https://www.wago.community/t/how-to-connecting-a-pfc100-pfc200-to-the-internet/121):
>
> Static IP Method: Switch the PLC to “STOP” and hold the recessed “RST” button down on the front of the PLC for 8 seconds until the system light begins to flash amber. The amber light indicates a change to a temporary static IP address of 192.168.1.17. Connect an ethernet cable between your computer and the PFC. Set the wired ethernet adapter on your computer to an IP address in the 192.168.1.X subnet (ex. 192.168.1.2). Use a web browser to navigate to 192.168.1.17 Log in with user: admin / pa…

---

<div class="post-metadata">

**Author:** ![Beker](https://avatars.discourse-cdn.com/v4/letter/b/f475e1/32.png) [@Beker](https://www.wago.community/u/Beker)\
**Post date:** [March 25, 2025, 9:11am UTC](https://www.wago.community/t/pfc-200-750-8212-unable-to-connect-via-ethernet-to-laptop-first-time-setup/1690/7 "2025-03-25T09:11:50Z")

</div>

Okey thank you. It helped. My computer now sees the PLC. My problem was that I did rst in Run mode. But I have another problem, Codesys can’t find my PLC, I downloaded everything from the Wago website and selected the right model in Codesys, and when I scan, it doesn’t appear

---

<div class="post-metadata">

**Author:** ![antauva](https://avatars.discourse-cdn.com/v4/letter/a/4bbf92/32.png) [@antauva](https://www.wago.community/u/antauva)\
**Post date:** [March 25, 2025, 9:20am UTC](https://www.wago.community/t/pfc-200-750-8212-unable-to-connect-via-ethernet-to-laptop-first-time-setup/1690/8 "2025-03-25T09:20:17Z")

</div>

Hello,  
try to type ip address directly without scan:

 ![image](https://us1.discourse-cdn.com/flex016/uploads/wago/original/2X/d/d8af5d3753e80fdeb0ba86c86cc6969fd4a94de5.png)

---

<div class="post-metadata">

**Author:** ![Beker](https://avatars.discourse-cdn.com/v4/letter/b/f475e1/32.png) [@Beker](https://www.wago.community/u/Beker)\
**Post date:** [March 25, 2025, 4:36pm UTC](https://www.wago.community/t/pfc-200-750-8212-unable-to-connect-via-ethernet-to-laptop-first-time-setup/1690/9 "2025-03-25T16:36:09Z")

</div>

![image](https://us1.discourse-cdn.com/flex016/uploads/wago/original/2X/b/b9388e53fb9765a0c30d45d4e27af59ec5ba2f53.png)

---

<div class="post-metadata">

**Author:** ![Beker](https://avatars.discourse-cdn.com/v4/letter/b/f475e1/32.png) [@Beker](https://www.wago.community/u/Beker)\
**Post date:** [March 25, 2025, 5:57pm UTC](https://www.wago.community/t/pfc-200-750-8212-unable-to-connect-via-ethernet-to-laptop-first-time-setup/1690/10 "2025-03-25T17:57:57Z")

</div>

Okey. I fixed it. It seams that I had to reinstall wago upload and add again wago Firmware PFC\_V040601\_28 when i did i started codesys and plc again and it connected. But anyways thank you all for help and support.