I highly recommend using the BACnet Configurator software along with the Codesys Add-on Solution Builder, both of which are available on the WAGO Download Center.

Here is a short guide that may help you get going: [How To: Add BACnet to a WAGO CODESYS project](https://www.wago.community/t/how-to-add-bacnet-to-a-wago-codesys-project/1626)

I consider this a much easier method than directly utilizing WagoSysBacnet, and gives access to a wider range of BACnet object types, including IntegerValue.

---