# Usage 750-652 with EtherCAT coupler

**URL:** <https://www.wago.community/t/usage-750-652-with-ethercat-coupler/2418>\
**Category:** Hardware and Linux\
**Tags:** how-to\
**Created:** [November 18, 2025, 6:15am UTC](https://www.wago.community/t/usage-750-652-with-ethercat-coupler/2418 "2025-11-18T06:15:22Z")\
**Posts on this page:** 6\
**Page:** 1

<div class="post-metadata">

**Author:** ![antauva](https://avatars.discourse-cdn.com/v4/letter/a/4bbf92/32.png) [@antauva](https://www.wago.community/u/antauva)\
**Post date:** [November 18, 2025, 6:15am UTC](https://www.wago.community/t/usage-750-652-with-ethercat-coupler/2418/1 "2025-11-18T06:15:22Z")

</div>

I want to use 750-652 module with EtherCAT Coupler.

Is there some way to create instance of

| `I_Port` | `WagoTypesCom.I_WagoSysComBase` | | |
| --- | --- | --- | --- |

to continue use FbMbMasterSerial function block?  
or at least FbSerialInterface?

---

<div class="post-metadata">

**Author:** ![Thruser](https://avatars.discourse-cdn.com/v4/letter/t/d26b3c/32.png) [@Thruser](https://www.wago.community/u/Thruser)\
**Post date:** [November 18, 2025, 7:16am UTC](https://www.wago.community/t/usage-750-652-with-ethercat-coupler/2418/2 "2025-11-18T07:16:27Z")

</div>

Hi,

check here [CODESYS Solution for Serial Comms via EtherCAT](https://www.wago.community/t/codesys-solution-for-serial-comms-via-ethercat/1684)

---

<div class="post-metadata">

**Author:** ![quenorha](https://sea2.discourse-cdn.com/flex016/user_avatar/www.wago.community/quenorha/32/429_2.png) [@quenorha](https://www.wago.community/u/quenorha)\
**Post date:** [November 18, 2025, 7:52am UTC](https://www.wago.community/t/usage-750-652-with-ethercat-coupler/2418/3 "2025-11-18T07:52:18Z")

</div>

You can use WagoSysFieldbusModule.FbModule\_75x\_652 library to create a I\_Port.

```auto
VAR
_abPi : ARRAY[0..47] OF BYTE;
_abPo : ARRAY[0..47] OF BYTE;
_oCom1 : WagoSysFieldbusModule.FbModule_75x_652;
END_VAR

_oCom1.SetNewPaInputs(ADR(_abPi),TO_USINT(SIZEOF(_abPI)));
_oCom1.GetNewPaOutputs(ADR(_abPo),TO_USINT(SIZEOF(_abPo)));

```

Where \_abPI and \_abPO are the process image of your 75x-652, from your EtherCAT communication, and \_oCom1 is the I\_Port you can simply use at the input of your function block.

---

<div class="post-metadata">

**Author:** ![Andrew](https://avatars.discourse-cdn.com/v4/letter/a/f19dbf/32.png) [@Andrew](https://www.wago.community/u/Andrew)\
**Post date:** [December 9, 2025, 9:12am UTC](https://www.wago.community/t/usage-750-652-with-ethercat-coupler/2418/4 "2025-12-09T09:12:08Z")

</div>

Hello, @quenorha

Does this method work with PLCs from other manufacturers? Is it possible to use WAGO libraries with other PLCs (Codesys 3.5) to work with WAGO EtherCAT couplers?

---

<div class="post-metadata">

**Author:** ![quenorha](https://sea2.discourse-cdn.com/flex016/user_avatar/www.wago.community/quenorha/32/429_2.png) [@quenorha](https://www.wago.community/u/quenorha)\
**Post date:** [December 9, 2025, 9:20am UTC](https://www.wago.community/t/usage-750-652-with-ethercat-coupler/2418/5 "2025-12-09T09:20:49Z")

</div>

Hello @Andrew,

As far as I know WAGO libraries are licensed for WAGO devices only.  
So I’m not sure.  
Maybe you can try importing the WagoSysFieldbusModule library in your CODESYS environment and check if you have license error while running it.

Which PLC do you use ?

---

<div class="post-metadata">

**Author:** ![Andrew](https://avatars.discourse-cdn.com/v4/letter/a/f19dbf/32.png) [@Andrew](https://www.wago.community/u/Andrew)\
**Post date:** [December 9, 2025, 9:27am UTC](https://www.wago.community/t/usage-750-652-with-ethercat-coupler/2418/6 "2025-12-09T09:27:14Z")

</div>

Xinje XSF5-A16

I need to connect to several WAGO EtherCAT couplers, which also have modules 750-652 installed.

Upd  
There is no errors

 ![image](https://us1.discourse-cdn.com/flex016/uploads/wago/original/2X/7/78c18c14f737609c9f0f93078d62b49fa9a503a9.png)