Wago PFC unexplained issue
We’re experiencing an unexplained issue with several PFC200 controllers. We connect to them remotely via VPN.
On several occasions, after uploading an application remotely, the download failed at 99%, and the transfer was interrupted. After that, communication with the controller was lost, and we were no longer able to connect to it. The device still responds to ping requests, but all other connection attempts (e.g. SSH or WBM) fail.
When inspecting the controller locally, we found that it had entered a state in which the WBM was no longer accessible. We also tried power cycling the controller, but that did not resolve the issue. The only way to restore it was by booting from an SD card containing a backup from another controller.
The application was downloaded without the “Create Boot Application” option enabled. The same application had previously been tested and successfully downloaded to another controller without any issues.
At the time of the failure, the PWR and I/O LEDs are green, while the RUN LED is red.
The problem also occurs spontaneously during normal operation, causing the controller to become unresponsive. As mentioned above, the only way to recover it is to restore the controller locally using an SD card.
We’ve already checked the CPU load and verified that all required licenses are installed.
Has anyone encountered a similar issue or have any idea what could be causing this?
Hi lukasz19,
Since the problem also occurs during normal operation, I would assume it has nothing to do with the VPN connection.
Which firewall is being used, how are the tasks configured, are BACnet, Modbus TCP, or OPC-UA communications running, and what is the RAM usage during operation? Are there cyclically called programs?
Issue description update:
Despite reducing the load on the controller’s CPU, the problem persists. This time, I was able to connect (I hadn’t noticed this before) to the controller at the facility via the CodeSys application (PLC SHELL and LOG). Although WBM is not running on the device, it is still possible to read individual parameters through CodeSys.
From the console, I forced the program to restart (stopprg, resetprg). The controller accepted the commands, but the WBM still did not unlock. Next, I forced a reset to factory settings, but that didn’t help either. After that, more errors appeared in the logs indicating a lack of licenses. Perhaps the memory became so corrupted that it even locked up the sections related to the basic licenses. At that point, it’s no longer even possible to upload the program remotely. The problem occurs every single time.
We do not have a firewall enabled on the controller. We use the Modbus TCP protocol to communicate with devices, and the controller also works with I/O expansion modules. The application is quite extensive—it includes, among other things, visualization, a PPC controller, MQTT communication, and other functions related to facility control.
We have already checked the task priorities and their execution times and did not notice any irregularities. During normal operation, CPU utilization does not exceed 80%, even at peak load.
Importantly, the same application running on a test controller in the office operates without any issues. We considered the possibility of voltage drops at the facility, but the controller operates within a wide range of supply voltages. Additionally, an identical application works correctly at another facility and on a different controller.
It also does not appear that the problem is related to the hardware itself, as the malfunction recurred after replacing the controller. At this stage, it is difficult for us to identify the source of the problem, and we are unsure how to proceed with further diagnostics.
Thanks for the insights.
I would check the local network (-> It is important that the same application runs without issues on a test controller in the office) and run a Wireshark capture on the second port of the PFC to see what traffic arrives there.
If the I/O expansion modules referred to are the 750-627 and 628, the field level can also cause a K-bus failure (indicated by the 750-628 showing a red LED instead of green).
Is the test PFC in the office equipped with the same I/O?
We are using IO 750-463/430/530 modules.
We have the same controller at our company, with the same input modules, and it works properly.
hello, are you doing online change or full download ?