Hi all,
I’ve encountered a potential (big) issue when it comes to the Modbus TCP configuration.
Hopefully there is something I’m missing in the configurator.
When a PLC goes to stop, exception, lose communication with I/O-node (750-362) the IOs are kept on the I/O-node even though I’ve set the parameters to “Set to zero”.
Does anyone have any experience with this?
For anyone struggeling with the same - Either you have to write/ set register 0x1001 or 0x1003 and use “Standard Watchdog Type” or use “Alternative Watchdog type” and set it directly on the coupler/ I/O-node.