750-673 Stepper Controller

On the WAGO 750-673 Servo Stepper Controller, does the ActualPosition value in the cyclic process image (D4–D6), accessed through FbStepperControlBasic.diActualPosition, represent the actual shaft position measured by the incremental encoder, or the internally calculated position based on commanded motor steps?

If the motor stalls or loses steps, will ActualPosition continue to reflect the encoder-measured shaft position? Is a separate raw encoder counter accessible via the mailbox interface?

The documentation doesn’t explicitly state that diActualPosition is directly from the encoder input, but that is likely the case.

I have sent an internal request to clarify. Stay tuned…

Some additional info:

“diActualPosition seems to be tied to how you set up your Pos_Mult and Pos_Div parameters. So, the position is essentially nebulous unless you structure your Pos_Mult and Pos_Div to be meaningful (like you should be doing). Also, if you force the position manually, the position change is not updated in diActualPosition.”

There are function blocks like FbSetPosition to force diActualPostion to a value you desire for rehoming or correcting mechanical errors.