How To: Setup the CODESYS Redundancy Add-on on a WAGO Controller using Modbus/TCP
This document outlines the steps necessary to set up a redundant system using the CODESYS Redundancy Addon with two WAGO controllers (in this case, two 750-8212 PFC200s). It shows the steps to configure two controllers to communicate over the redundant link, synchronize the PLC scans, and share redundant data. At the end of the document, it shows an example program that demonstrates the use of Modbus/TCP as the redundant protocol for communication with a fieldbus coupler.
HOW TO - Setup a Redundant WAGO Controller System.pdf (1.9 MB)
can you share codesys 3.5 program with us with library?
Attached is the project I used to test the redundant functionality.
PFC8212RedundacyWithModbusTcpCoupler.project (342.1 KB)
Please also note that Wago has published a guiding video for using CoDeSysRedundancy:
https://www.wago.com/global/lp-onlineseminar-codesys-redundancy
Is it possible to share the program/fb that is used in the online seminar?
Will CODESYS Redundancy Addon work with 2 Edge Controllers (752-8303/8000-002)?
I was told by the Product Manager that the CODESYS Redundancy license (2759-245/211-1000) is compatible with the TP600 and the Edge Controller too.