IPC Linux Codesys Runtime SL Save Retains
It seems that on the Codesys Linux Runtime SL with Version v3.5.21.2 the retain variables will save when you perform a graceful shutdown (from CLI or WMB) but not if you cycle power. One way to remedy this is to save the retains to a file and periodically save these off, and then subsequently load this file on startup. Here is example code to do this if it is needed.
PROGRAM RetainSaveProgram
  pApp : POINTER TO APPLICATION;
  sRetFile : STRING := ‘MyAppRetains.ret’; // file
  nameresult : CmpErrors.RTS_IEC_RESULT;
  res : DINT;
  TSave : TON;
  xFirstScan : BOOL := TRUE;
IF xFirstScan THEN
  xLoad := TRUE;
END_IF
IF xSave THEN
  pApp := CmpApp.AppGetCurrent(pResult := ADR(result));
  IF pApp <> 0 THEN
    result := CmpApp.AppStoreRetainsInFile(pApp, sRetFile);
    IF result = 0 THEN
      xSave := FALSE;
    END_IF
  END_IF;
END_IF;
TSave(IN := NOT TSave.Q, PT := T#300S);
IF TSave.Q THEN
  xSave := TRUE;
END_IF
IF xLoad THEN
  pApp := CmpApp.AppGetCurrent(pResult := ADR(res));
  IF pApp <> 0 THEN
    res := CmpApp.AppRestoreRetainsFromFile(pApp, sRetFile);
    IF res = 0 THEN
       xLoad := FALSE;
    END_IF
  END_IF;
END_IF;
xFirstScan := FALSE;
Here are the two libraries you need to add to your project.
Screenshot 2025-09-19 at 7.31.25 AM