I have checked the link about OPC UA certificates:
However, I keep getting error messages when trying to generate them.
I have verified that the clock is correctly set on the device.
I have tried generating the certificates while being connected to the device and while being disconnected.
I have flashed the CC100 PLC with new firmware 04.06.03(28), but the issue persists.
Is anyone else able to generate OPC UA certificates on the CC100?
Hello espenbo,
i would set the controller to Stop when creating the certificates. Depending on how busy your controller is, the certificate creation in Run may not work.
GDS push only works with e!COCKPIT based firmware and the WAGO OPC UA Server. The CODESYS OPC UA Server doesn´t yet support this function. According to the CODESYS RoadMap, the function will be implemented with V3.5 SP22 (2026).
CC100 → does not work, as only CODESYS-based firmware exists here
PFC 100 G1 (750-810x) → works with e!COCKPIT based firmware
PFC 100 G2 (750-811x) → does not work, as only CODESYS-based firmware exists here
PFC 200 → works with e!COCKPIT based firmware
PFC 300 → does not work, as only CODESYS-based firmware exists here