PFC200 (750-8212) OPC UA Data Source drops connection with 0x80AD0000 although server responds normally

Hello,

We use the CODESYS OPC UA Data Source (Data Source Manager) on a PFC200 to connect to three external OPC UA servers. Each connection drops at random intervals, roughly every 1 to 3 hours per connection, and reconnects after about 24 seconds. A network capture shows that the server responds normally, and that the PLC closes the connection itself.

System

  • Controller: WAGO 750-8212 PFC200 G2 2ETH RS XTR
  • Firmware: 04.07.03(29), codesys3 6.4.2.3
  • DatasourceOpcUa 4.6.1.0, DatasourcesMgr 4.6.0.0
  • Three OPC UA Data Sources (Framo_1..3), about 1300 variables in total. Security mode None. Subscription with a 500 ms publishing interval. The application writes a REAL setpoint about 2 to 3 times per second, and a heartbeat about every 3.6 s.
  • The servers are open62541-compatible Python servers (asyncua 1.1.6) on the same subnet.

Symptom (runtime.log)

CmpOPCUAStack  OpcUa_Channel_ResponseAvailable: Request failed! (0x80AD0000)
DatasourcesMgr Framo_1: Sending request failed with errorcode: Failed (20)
DatasourcesMgr Framo_1: Error Failed (20) in state Ready
(24 s later)
DatasourcesMgr Framo_1: Connection established

This happened 7 times in one night, spread over all three data sources. The system log (/var/log/messages) shows no network or kernel events at those times.

Network capture of one drop (tcpdump on the server side)

Time (s) Direction Message
0.000 PLC → server PublishRequest (normal, a new one after every PublishResponse)
0.289 PLC → server WriteRequest (1 node, Double)
0.291 server → PLC WriteResponse, ServiceResult Good, result Good
0.399 PLC → server CloseSecureChannel (CLO), initiated by the PLC
0.400 TCP FIN from both sides

In the 45 seconds before the drop, all PublishResponses arrived exactly every 500 ms. All write responses arrived within 0.5 to 2 ms. There were no errors or gaps. Secure channel renewals (OPN) every 45 minutes worked normally on all three connections, and the drop did not coincide with a renewal.

The OPC UA stack therefore reports Bad_Disconnect (0x80AD0000) for a request even though the server neither disconnected nor returned an error. The data source then closes the channel on its own.

In an earlier session (after a download) we also saw CmpOPCUAClient *EXCEPTION* in tasks OPCUAClient_2b2 and OPCUAClient_2ad.

Questions

  1. Is this a known issue in the OPC UA client stack or the Data Source for this firmware/runtime version? Is there a firmware or DatasourceOpcUa version that fixes it?
  2. In which situations does OpcUa_Channel_ResponseAvailable report 0x80AD0000 when the server has not disconnected? For example: an internal request timeout, a request queue limit, or concurrent requests (a pending Publish together with a Write).
  3. Can the reconnect delay of about 24 s be shortened in the Data Source configuration?
  4. Are there settings that make the Data Source keep the session after a single failed request, instead of closing the secure channel?

The PLC clock was not synchronized during the test: the date was 2026-03-14, and the clock was about 36 s fast. We will set up NTP. Could the clock difference matter for the client stack, given that the server time was 2026-11-06?

I can provide the complete runtime logs and the pcap file.

Best regards,

Put your OPC items all in a separate Task set at least double of cycletime than de OPC Task is using.

When tags are needed in other tasjes put those in a GVK application