Hello all,

I’m designing a redundant alarm and monitoring system (marine application) and would like advice on how the SCADA side should connect to a redundant PFC200 pair.

Setup

  • 2 × PFC200 G2 (750-8210) running CODESYS Redundancy (active/passive), with a direct redundancy link between them
  • Field I/O: 3 × 750-362 Modbus TCP couplers, daisy-chained between the two PLCs
  • Two independent networks, each a Moxa EDS-518E Turbo Ring:
    • Network A: 172.16.x.x → X1 of both PLCs
    • Network B: 172.17.x.x → X2 of both PLCs
    • X1/X2 in separated mode (no bridging between A and B)
  • SCADA: Ignition, 2 redundant servers (Linux), connected to both networks, reading the PLCs over OPC UA

Problem
Each PLC has its own IP on each network, so SCADA sees 4 endpoints (PLC1-A, PLC1-B, PLC2-A, PLC2-B). As far as I can tell, CODESYS Redundancy does not give the pair a shared/virtual IP, so SCADA has to work out which PLC is active and which network works.

My idea
Have the active PLC take over a shared service IP on each network:

  • Fixed IPs: PLC1 = .21, PLC2 = .22 (on both networks)
  • Service IP .20 on X1 and X2, held only by the active PLC
  • On becoming active: add .20 (e.g. ip addr add via SysProcessExecuteCommand) and send a gratuitous ARP. On becoming passive: remove .20
  • SCADA then uses one OPC UA connection: endpoint 172.16.0.20, failover endpoint 172.17.0.20

Questions

  1. Does WAGO or CODESYS offer a supported way to get a shared/virtual IP for a redundant PFC200 pair? Does Application-Based Controller Redundancy (ACR) handle this?
  2. Can SysProcessExecuteCommand on the PFC200 run ip addr add/del and arping? Which runtime config settings are needed, and are there firmware restrictions?
  3. Is the CODESYS OPC UA server reachable on an IP alias added at runtime, or does it only bind to the configured interface IPs at startup?
  4. If the redundancy link is lost, both PLCs go standalone. How do others prevent both PLCs claiming the service IP, and both writing to the Modbus couplers?
  5. Has anyone connected a redundant PFC200 pair to a SCADA system (Ignition or other) over two networks? What worked for you?

Firmware/CODESYS versions: FW30

Thanks in advance for any experience or advice.