750-657 Question

750-657 Question

Hello, this is Matthew Kim from Korea.

A client contacted us stating that while the existing sensors on the 750-657 card are working, the system is not functioning even after attaching new sensors and adding an IODD.

I initially responded assuming it was a simple on-site setup issue, but I have confirmed that it is impossible to connect other IO-LINK sensors to the 750-657 units at our company.

Since I have previously tried connecting it with a 750-1657, I would like to inquire if this phenomenon is occurring due to hardware differences that I am unaware of.

I am aware that the 750-657 is an older, discontinued model, but I am currently investigating whether this is a matter of my expertise or if there is another underlying cause.

750-657 Question Sensor ZSE20B-L-P (SMC) that was connectable at the customer’s site

Sensor ISE20B-L (SMC) that was not connectable at the customer’s site

My internal test products Q4XFKLAF610-Q8, LE550-KQ (Banner)

The reason I am asking about the above matters is that we know the cause of the problem, and this is to provide reliable feedback to the customer.

Hello,
I know 2 thing:
First the 750-1657 have an automatic configuration capability, the 750-657 don’t have.
The 750-657 should not have the parameter server enabled.

But I haven’t found a IO Link sensor that can’t be connected to our device…