Client Configuration in WAGO Telecontrol Configurator

I am using the WAGO PFC200 controller (750-8212/0025-0002) with firmware version 04.05.10(27) and programming in CODESYS 3.5 SP19 Patch 7. I am configuring an IEC 61850 client in the WAGO Telecontrol Configurator (version 1.4.12.4) and have several questions and concerns regarding the configuration:

  1. Limit of 2000 Tags/Objects:
    The configurator appears to have a limit of 2000 tags/objects. Is it possible to increase this limit, for example, by modifying some configuration file? How can I handle cases where I need to configure more tags than this limit allows?
    image
  2. Selecting Tags from DataSets:
    When selecting tags to read from a slave, I can only choose entire DataSets without the ability to select individual tags within a DataSet. This results in reading unnecessary tags, which consumes part of the 2000-tag limit. Is there a way to configure only specific tags of interest, bypassing the rest of the DataSet?

Hello

First of all, it is not possible to increase the number by changing the parameters from the configuration files and not suggested as well.

Last but not least, you need to filter data from IED itself. Could you please also try the latest version for telecontrol configurator? might be some changes and updates on that about choosing dataset but with the current version you choose is not possible to select individual tags from dataset.

Thanks

When replacing PFC200 with PFC300 (750-8302) + Telecontrol License, up to 5,000 data points can be used.