CODESYS V3 Ethernet Driver

The attached document explains how to use the CODESYS V3 Ethernet driver with a WAGO PLC and a compatible HMI.
Using the CODESYS V3 Ethernet driver on a WAGO PLC.pdf (1.4 MB)

5 Likes

This is very good guide. I was trying same this today, but did not get success. Will try your guide next week. I was missing to tick “Link Always” also have not downloaded the program to PLC after creating Symbol Configuration.

I am trying with Webaccess/HMI runtime.

Thank you for the write-up!

How would you go forward changing persistent variables with this method (as set points are usually stored in PersistentVars and this cannot be accessed in “Symbol configurator”)?

PersistentVars can be included in the export file. For example, create some persistent data:

Check the “Link always” option:

Check the variables in the Symbol Configuration:

Compile the project and then the persistent variables appear in the export file: