Configuration 750-652 on PLC 750-8111

Hi all, im new about wago word but not about PLC.

Is my first time about programming a WAGO PLC and im founding some problem about the HW configuration.

I have a PFC100 750-8111 PLC with 2 modules: 750-1405 and a 750-652; in in Kbus configuration i made the search and the system found both of the modules, but when i try to download the configuration into the PLC i receive the error message about the IOSTANDARD and from the diagnosis i see the error about the Kbus configuration.

All the led on the PLC are green and the positioning in the tree config is correct PLC-> DI → SERAIL → END MODULE

I finished the idea about what to try and test

Can you share a screenshot of your KBUS configuration? You may also try right clicking the KBUS in the device tree, and scan for devices. From there you can copy the IO into your project.

i was able to solve the problem. At the end the problem was related to the verison of the library in the project, the newest library of IO Standard for some reason was not working with my module. i changed with on old rev. and now is working