EtherCAT Distributed Clocks
Configuration:
  • CODESYS V3.5 SP19 Patch 7
  • WAGO Edge Controller 752-8303/8000-0002 FW27
  • Beckhoff EKM1101 EtherCAT Coupler
  • 2 X Beckhoff ELM3002_0205 2-channel analog input
Are there any examples on using distributed clocks with EtherCAT modules? I have successfully imported the appropriate EtherCAT Slave device repository files and configured an EtherCAT master, EKM1101 EtherCAT Coupler, and Analog Input slices to operate synchronized to the edge controller at a task period of 1.25ms.
Now I am trying to setup oversampling with distributed clocks so that the synch unit cycle is 78.125us (/16) but getting errors and getting stuck transitioning out of PRE-OP mode. I believe it is an issue with my “DC Cyclic Unit Control…” Settings but the wiki is lacking descriptions for these inputs. See attached images of EtherCAT Master log and slave configurations.
The following settings allow for EtherCAT OP-mode but when sampling a 110V 60Hz sine wave it appears that the communication link is interrupted and latches the last valid measurement until communication is restored.
Plot of the average of the 16 oversampled measurements. Shown cursor delta time of 66.386ms
It seems I was running into two different issues in my testing: CPU limits and attempting to operate with a EtherCAT task period that was faster than the cycle time of the installed modules. This caused Rx Frame Count and Frame Lost Count to increment and the EtherCAT CPU load would reach 100%. This is a known limitation with the ARM processor I was using and was functional after increasing the task period from 1.25ms to 5ms. I will be looking into different intel processor controllers that are capable of running faster EtherCAT taskrates.
As for the ELM3002 configuration, it seems that the distributed clock settings do not need to be explicitly configured in the “General” tab. Instead, when selecting the channel number of samples in the “Process Data” tab the device will automatically configure its internal distributed clock accordingly based on the EtherCAT task period (DC_period=ECAT_period/num_samples). If the user attempts to set a DC_period faster than the minimum (100us in the case of ELM3002) then the EtherCAT_Master Log will show an invalid DC Settings message during PreOP.
In addition, it is not explicitly stated in the manual, but in order to reduce the EtherCAT CPU usage and increase the number of oversampling then the “Process Data” must specify the data in Integer format (16b) as opposed to DINT (24b) or real (32b). The measurement linearization must be changed accordingly.
Just an additional hint when setting up EtherCAT on WAGO Controller, make sure you disable Broadcast limitation in the configuration of Ethernet interface in the WBM.
Disabling Broadcast limitation improved results and decreased CPU load slightly but still the 752-8303 multicore was having intermittent Rx Fr losses. CODESYS EtherCAT 4.9.0.0 claims to have some optimization improvements as well. I will test with it next, but still looking towards an intel cpu alternative
You might try the new PFC300 which has a faster CPU than the Edge Controller.
PFC300 (750-8302)
Dual Core Cortex A53 1.4 GHz
2x GbE
Edge Controller (752-8303/8000-002)
ARM® Cortex® A9 Quad-Core 1.0 GHz
2x 100 MbE
Not sure if it still relevant, but in my EtherCAT research I found this study from texas instruments with Codesys 3.5.19.10 mentioned that selecting CPU 1 as the EtherCAT task showed CPU spiking improvements over the performance of cores 0, 2, and 3.
Hello Kurt, the released version of the PFC300 is 1.4GHz
the pfc 300 will show the same behavior.
It will be great when czeck can confirm this.
We currently only have PFC200 and Edge Controllers at our facility. We are proceeding with a 12th generation intel I7 solution instead since we anticipate needing to operate multiple fast EtherCAT tasks. Currently waiting on lead time of shipment.
Confirmed that the issue was CPU limited. Intel 12th Gen i7 used (8 performance cores, 4 efficiency cores). I am achieving send and recieve times consistent with codesys help pages (<10us). After following the page’s recommended performance optimization.
Plot of 60Hz first sample and number of samples per task (10 samples per 1ms task)
EtherCAT is on core 3. Processor load peaks are around 40%