hello,
Yes they are shorted together
Hello
Iâm working on the same topicâI have n Socomec meters connected in âRS485â series, and Iâm going to use the Wago 750-1652 card to read the various values.
I found this tutorial that might help us; on my end I still get a read error and I donât know why, even though I followed the video closely.
Wago 750-8212 Modbus RTU Master \u0026 Third Party slave in Codesys 3.5
Feel free to get back to me if youâve made any progress on the topic.
You can also do settings of the IO card with the WAGO IO-check software.
Maybe this can be checked also.
This is how I did it with a VEGA sensor:
Variables:
FbMbMasterSerial_Vega: WagoAppPlcModbus.FbMbMasterSerial := ( xConnect := TRUE,
udiBaudrate := 9600,
usiDataBits := 8,
eParity := WagoTypesCom.eTTYParity.None,
eStopBits := WagoTypesCom.eTTYStopBits.One,
eHandshake := WagoTypesCom.eTTYHandshake.None,
ePhysical := WagoTypesCom.eTTYPhysicalLayer.RS485_HalfDuplex,
eFrameType := eMbFrameType.RTU,
tTimeOut := T#200MS
);;
utQueryVEGA : typMbQuery := ( bUnitId := 246, // Slaveaddress
bFunctionCode := 16#04, // read input registers
uiReadAddress := 1300, // Startaddress
uiReadQuantity := 11, // Quantity of wanted registers
uiWriteAddress := 0, // not needed for FC4
uiWriteQuantity := 0, // not needed for FC4
awWriteData := [124(0)] // not needed for FC4
);
xTxTriggerVEGA : BOOL; (* Set this variable once for start a job.
This variable will be automaticly reset by the master
if the job is done.
*)
utResponseVEGA : typMbResponse; (* After the job is done you can find at this structure
the result.
*)
Yes they are still connected as the picture, the total resistance is 60 ohm
Normally I would try now to check the communication with an USB-RS485 adaptor and a PC.
First, if the meter is responding to request wit programs like modbus poll or qmodmaster.
Then, if the PLC is sending requests. For this only a terminal program with ability to show hex data, e.g. realterm, is required. Also if the meter is responding to the request you can see then.
Some meters have a time limit for requests, between requests have to be several seconds.
Okay thank you for your help Thruser, I will check this
Is the ground necessary ?
I have âerror time outâ uid:153
Also, I have these symptoms on the module :
-
The C / Rx LED is off
-
The B LED is yellow
-
The E yellow LED indicates RS-422 duplex mode
Hi, you have to use half duplex mode, not full duplex, as you have only two wires. Modbus RTU with RS-485 is normally half duplex. That I have missed.
Hello,
For the 750-1652 card, we agree that thereâs no need to add resistors, as they are internal. Similarly, for wiring, thereâs no need to make a connection between pin 1 and pin 3 (same for pins 5 and 6).
Thank you in advance.
Hi,
According to the manual it is possible to activate an internal termination resistor and/or BIAS resistors.
This has to be done via WAGO I/O Check. It seems you can also set this within program code
For half duplex mode the connection between RX and TX pins should be internally made, so no external wiring is required.
Had the same issue, I used code code to read out the data instead of a modbus device.
Pins 1 and 2 and pins 5 and 6 need to be connected.