Hello everyone, I’m new here
and I’m coming straight to a problem for which I currently have no further approach (I’m a bit lost) and I’m hoping for your support and/or experience ![]()
I have already read some posts about Modbus RTU here… ultimately without success
This is my first connection of a Wago PFC to Modbus RTU and also the most tedious one.
- Controller PFC100 (750-8112) FW04.06.01 (28), CodeSys 3.5 SP19
- Modbus RTU on local Sub-D, Mode Serial Interface (in PFC to RS485)
- Connector on SUB-D Wago 750-960, termination resistor switched on
- In the HW Config, only one Modbus slave was created (see screenshot)
- Slave Addr.3 (three registers (channels) created)
When the controller is loaded and started, a bus error is displayed for Modbus (time out - no response).
The Modbus slave (eletechsup NT18B07) can be addressed, configured, and the register values can be read via ComTest Modbus (on a notebook). Connection via USB-RS485 adapter.
I assume that since no communication is established, there must be some kind of configuration or hardware error?
No application has been created yet (no FBs available to read the registers); I think it’s pointless as long as communication is not established?
What has already been tried…
- Different CodeSys version (3.5 SP19)
- Swapped lines A and B
- Tested directly on Pin 3 and Pin 8 in the socket
- Termination resistor at sensor 120 Ohm
- Shielded (longer) cable
Here is a screenshot of the ModbusDevice Addr.3…
Here is the configuration and error…
I hope you still have an approach for me on what I can test/change that will lead to success. If further information is missing or would be helpful, please let me know briefly - I will provide it immediately. (If more productive, feel free to do the whole thing in English)
Thank you very much in advance for your help