Hello everyone, I’m new here :raised_hand: and I’m coming straight to a problem for which I currently have no further approach (I’m a bit lost) and I’m hoping for your support and/or experience :flexed_biceps:

I have already read some posts about Modbus RTU here… ultimately without success :face_with_raised_eyebrow: This is my first connection of a Wago PFC to Modbus RTU and also the most tedious one.

  • Controller PFC100 (750-8112) FW04.06.01 (28), CodeSys 3.5 SP19
  • Modbus RTU on local Sub-D, Mode Serial Interface (in PFC to RS485)
  • Connector on SUB-D Wago 750-960, termination resistor switched on
  • In the HW Config, only one Modbus slave was created (see screenshot)
  • Slave Addr.3 (three registers (channels) created)

When the controller is loaded and started, a bus error is displayed for Modbus (time out - no response).

The Modbus slave (eletechsup NT18B07) can be addressed, configured, and the register values can be read via ComTest Modbus (on a notebook). Connection via USB-RS485 adapter.

I assume that since no communication is established, there must be some kind of configuration or hardware error?

No application has been created yet (no FBs available to read the registers); I think it’s pointless as long as communication is not established?

What has already been tried…

  • Different CodeSys version (3.5 SP19)
  • Swapped lines A and B
  • Tested directly on Pin 3 and Pin 8 in the socket
  • Termination resistor at sensor 120 Ohm
  • Shielded (longer) cable

Here is a screenshot of the ModbusDevice Addr.3…

Here is the configuration and error…

I hope you still have an approach for me on what I can test/change that will lead to success. If further information is missing or would be helpful, please let me know briefly - I will provide it immediately. (If more productive, feel free to do the whole thing in English)

Thank you very much in advance for your help

Hello

The integrated serial port into the controller has a dual electrical interface RS232/RS485 and by default it assigned to RS232. You need to confirm first the port is using the right interface RS485. This have to be done manually thought the WBM (web configuration pages) under the “Configuration” tab go to menu: “Administration | Serian Interface | Assign Mode of serial interface“, select “RS485”, submit and reboot the controller (not sure if the later is required)

Hello Alfonso, first of all, thank you for your response :+1:

I had already set the COM in the PFC to RS485…

Unfortunately, in the online monitor, the bus connection keeps switching to “Not running.” Next, I will obtain and test another Modbus device.

Best regards, Mattes

Welcome!

-Did you check the ‘auto-restart communication’ on the client settings? It’s a good idea for easy startup.

If it still doesn’t work could add a few screenshots of your modbus settings.

Hello MAD2026,

Perhaps this helps:

CodeSys has renamed the Master and Slave.

These are now called Master => Client and Slave => Server.

You can also see this in the last screenshot from Wago above.

Best regards

Hello, first of all thanks for the answers :+1:

Here is the input regarding this:

  • Yes, the configuration is set to RS485 on the PFC (configured via WBM)
  • The “Restart” communication is also active
  • Yes, the client/server setup is confusing (but it is plausible given the configuration options)

Here are the requested screenshots (offline and also online (status)):

According to the error (Server Status), no reply is received (no Reply in Time). This can also be observed after increasing the Response Timeout to 5 seconds following a reset.

The next attempt will be to use a different sensor (different type) — let’s see what the port reports then :man_shrugging: It’s surprising that the sensor currently communicates flawlessly via tools like Commix or ComTest…

Device Configuration

Modbus_COM_Port

Modbus Client_COM_Port

Modbus Server_COM_Port

Thanks in advance to everyone — I will keep you updated :victory_hand:

Best regards, Mattes

Before you wrote that Modbus Device addr is 3, but now in the screenshots server-adress is 1..
Did you check this?

Hello Antauva,

Yes, that is correct. I initially tested with address 3 (without success), then performed a reset to default and continued testing with address 1. Address 1 is correct (identical in the configuration and the address set on the device).

Best regards,
Mattes

Ok, my advise, start use FbMbMasterSerial from WagoAppPlcModbus library.
In this library you can find more detailed diagnostic information.

Now we can see only Error code - Response Timeout.
Can you connect PLC COM to USB-RS485 Com to notebook, to check what Wago PLC try to do with serial com?

Hello @MAD2026

I have faced this kind of issues with different modbus RTU slaves before. Generally it was about the bias networking in modbus rtu line ends. I mean, if the slave device does not have pull up - pull down resistor between Vcc-D+ and between GND-D-.

Normally in most cases 750-960 will enough for you to have biasing due to it has 390 ohm in both side ( up and down ) with ending resistor but resistor will not neccessary due to the line is short in your setup I assume.

If nothing helped you, I recommend you to try at least 1k ohm instead of 390 ohm at both pull up and pull down resisting. This maybe shows you what is the main problem. You can easily take 2 pcs of 1k ohm resistors (smd or not) and connect to DB9 connectors (standart connector) pins. You can check our manual which ports are what.

3 –> Data +

5 –> GND

6 –> Vcc (+5V)

8 –> Data -

Please test and give us your feedback.

Best Regards!!

Hello @MAD2026

My experience is that Modbus is a simple protocol but, when working with a new slave/device usually is hard to have results at the beginning, mainly because we do no have tools or enough information to figure out what the communication is not happening. I am confident that at some point you’ll have it working. I do not think it may be a problem with the version of Codeysy or the firmware in the PLC.

The most important thing is you already have a good starting point: you are able to exchange data between the device and the PC!. So i can asume that the cabling and bus termination are god enough. My next step would be to confirm connect the PFC100 in parallel and configure it to act as a SLAVE, traying to read a single register form the PC would be enough to check the pin connection and the polarity. I suppose you have a software in the PC to make request, if not I typically use “OpenModScan” (you can download it from Github), it is free an simple to use. In the PFC100 i would configure a couple of channels: 5 single Holding Register and another 5 Input Registers, both starting from address 0. Set different values to any of the register and then try to read one single register with address 1. This trick will save you to deal with the Mosbus/Modicon Addresing mess.

You can try to configure the PLC as a master an use a program in the PLC to see the bytes of the Mosbus messages. I use CoolTerm (free software) because it can show the incoming data in binary format. If your are familiar with Modbus protocol you can confirm that he transmission parameter and the polarity are correct. For this test configure a shot message as reading a single Input register with a low pooling time, one second or slower.

I am confident you’ll make it work!!

Best regards

Hello everyone, first of all, thank you for the answers and valuable tips :+1:

I have now connected another device (a different sensor type) - unfortunately with the same result >> once the controller is loaded and started, a bus error (time out - no response) is displayed for Modbus :worried:

Next, I will follow your recommendations and use the diagnostic FB FbMbMasterSerial. Unfortunately, I have absolutely no idea (at least in CFC) what needs to be connected as input.

The documentation I found doesn’t help me at first glance; I first need to understand the various configurations defined as arrays, queries, or structs (how and where variables need to be defined or created there).

I somehow couldn’t find a good description of the FB indicating exactly which input must be connected to what. So for now, I’ll keep searching and integrate the FB correctly. (I recently found one or two examples in Structured Text online; I’ll take a look at them).

In parallel, I’ll try adding the resistors on the sensor side, even though various tools via USB-RTU adapters exchange data with the sensor without issues.

Still unclear for me: Does the RTU node in the HW configuration need to turn green in the online view? Regardless of whether a program is running or not… if it still reports a time out (and that even without running software), won’t an FB provide any further information?

Unfortunately, I have very little time in the coming weeks to test this online with the hardware… but I’ll keep at it.

Many thanks for your input (and patience).

Best regards,
Mattes

Hello.

I am DohyunKim, living in South Korea. You can call me Matthew.

Anyway, I became interested after reading your post, so I conducted a similar test.

I used the 750-8214 and connected it to a PC via a 485 USB to perform a Modbus RTU test.

I understood that terminating resistors are not necessary for 485 communication over short distances, so I experienced symptoms similar to yours when I tested without them in a past 485 test.

I checked again to see if RTU communication might be affected by the terminating resistor, and the results were identical.

It appeared that packets were being exchanged successfully on the PC Modbus RTU Slave, but Codesys could not receive any data.

Conversely, the same result occurred when the PC became the Master and Codesys (750-8214) became the Slave.

When checking the raw data on the Slave, it appeared that reception was successful but transmission was not, and the same was true in the opposite case. What I am focusing on is that you used a ProfiBus DP connector on one end and a 120-ohm resistor on the other.

I am mentioning this because ProfiBus DP uses 390 or 220-ohm resistors, whereas the 485 uses a 120-ohm resistor, and I suspect this may have had an impact.

In fact, when I tested without using resistors, I experienced the same symptoms as you, but I confirmed that communication worked without issues when I attached 120-ohm resistors to both ends.

Actually, communication did work when I added an additional 120-ohm resistor to one end (combining 240-ohm and 120-ohm resistors), but I do not think this can be considered perfect or stable.

I focused on the fact that the 485 termination resistor is 120 ohms, while the 750-960 termination resistor is 220 ohms.

I would appreciate it if you could provide feedback on the results.

I hope it is not too late.

Hi Matthew, I received your post and I am happy to pick up additional information.

I will procedd with the RTU Topic the next week - in menatime I received an new SUB-D Plug without embedded Resistors to check the function with other vlues (as you descibed)

I keep you informed and come back if I have additional questions concerning th etools you have used to read the RTU communication

Thank you - your input is extremely useful and is greatly appreciated.

BR

Mattes

Hi MAD2026.

I have attached an example of the code for the WagoAppPLCModbus with Serial communication here. Hope it helps you :slight_smile:

Saved in CS3.5 SP21 Patch 3

Best Regards Jan

Modbus_Example_V01062026.project (814.6 KB)

Hello.

The termination resistor related to the “characteristic impedance” of the cable and it determined by the its constructive characteristics. Typical values for twisted pair cables are between 120 and 160 ohms where for coaxial cable may be 50 Ohms. If a cable run is not matched with its characteristic impedance (of the connected device) then energy of the incoming signal will bounce back to the cable affecting (distorting) to the incoming signal. This effect will be more critical when increasing the speed (baudrate) and/or the length of the cable. In Profibus the value of the resistor is, as in Modbus, around 120 Ohm, not because both protocols use same electrical transceiver , RS845, but same type of cable: twisted pair. There is two ways do the termination using a single resistor or three resistor combined with 5 volts (“fail-safe termination”) but in the latter the equivalent value will be again about 120 ohms.

Commonly people feel that they do not need a terminating resistor for short cables at 9600 bps but my recommendation is to use one resistor in parallel, not just to terminate the cable but to “consume” the electrical noise coupled in the cable: In the bus when all RS485 drivers are in high-impedance (nobody is transmitting) the cable acts as an antenna picking-up the noise generated by the mains and it may induce some communication errors. You can see this 50hz noise easily with an oscilloscope.

I also found that there are some devices that are (probably they are not properly developed) require a “fail-safe termination” (biased) to work properly

Texas Instrument has this application note that is considered the Bible of RS485

AN-1057 Ten Ways to Bulletproof RS-485 Interfaces (Rev. B)