I’m trying to connect to a basic controller 100 in codesys and I get nothing.
current setup is jumper ip
firmware 04
codesys 3.5.19.7(tried 32 and 64 bit)
device description basic controller 1.0.4.13
device description 2.0.6.8
I can ping the thing, I can access the web frontend, but I cant connect to it in codesys, just nothing. tried it run or stop, tried all three firmwares, nothing. I cant think of anything else I can do. Any help would be great.
What error message are you getting in CODESYS?
Is your IO LED blinking red?
Also, the Basic Controller requires at least one IO module and an End Module to be a valid node - otherwise, it will not connect with CODESYS.
io is green, its running a single 750-652 and a 750-600. plc will Run from the web frontend. codesys error is “Scan Failed, Please check the gateway is running and that its settings are correct” firewall is off, I can ping it, and connect to the web frontend from the codesys machine.
It sounds like the CODESYS gateway is either not set up or not functioning correctly. You should be able to scan the network from the screen below. After scanning and selecting the PLC, both the gateway and the PLC should display a green icon.