How to read Modbus RS485 on plc

Hi,

According to the manual it is possible to activate an internal termination resistor and/or BIAS resistors.

This has to be done via WAGO I/O Check. It seems you can also set this within program code

For half duplex mode the connection between RX and TX pins should be internally made, so no external wiring is required.