Hi,
These are not two servers, but two different endpoints. One with hostname and one with the IP in the endpoint URI’s
Your last picture looks good … normally you only have to look in the quarantine folder from your controller in the security screen and then put the certificate from the client to the trusted folder via drag&drop.
It worked once I moved the certificate from quarantine to trusted.
I have an error when connecting, if I press ignore a poll occurs. What is this error and how to treat it?
Hi,
the error refers to the SubjectAlternativeName extension, which shall contain the server’s hostname(s) and/or IP addresses. If you connect to the server using it’s IP address and the certificate only contains the hostname (or the other way round), this error will be thrown.
I’m trying to communicate the Prosys OPC UA Simulation Server with the Edge Controller (FW26) configured as a OPC UA Client with the DataSourcesManager
Everything seems to be normal using the ControlWin but not with the edge controller
Is there a configuration to do?
I’m using opc.tcp://ipaddress and not the devicename and my CODESYS Communication is updated as 4.5.1.0
I’m using the embedded OPC UA server on a Wago PLC running Codesys.
Is there a way to restart the OPC UA server without restarting the PLC?
I am moving certificates from my PC directly into the trusted folder in the linux file system, and the certificates work, but only after a PLC reboot.
You can restart only the runtime but I don’t think you can restart only yhe OPC UA server.
You can restart the runtime from the WBM, Fieldbus / OPC UA.
Thank you for the reply. I’m not using the OPC UA server configurable from the WBM, I think. There is a difference between this and an embedded OPC UA server, as I understand it.
I’ll try to attach an image to show, that the OPC UA in WBM is not active.