Unresolved External POUs Error on 750-8202/8 with Cloud Library

Hi everyone,
Hi everyone,
I am currently working on a WAGO 750-8202/8 controller and using a cloud library in my project. I am using Firmware Version 22.

While trying to download the program to the PLC, I encountered the following error:

The error says:

I also tried changing the directory of the library, but unfortunately, that did not resolve the issue.

Could someone please guide me on what might be wrong? Am I missing some library dependencies or configuration steps?

Any help would be highly appreciated!

Hello,
Unfortunately It seem the Cloud Connectivity support of Codesys 2.3 was dropped after the FW17 …
Now there is 2 solution:
Roll back to FW17,
Upgrade to e!Cockpit

Hi @WagoIcard
I have current firmware 22. Should I roll back to FW 17?

how can i upgrade 750-8208 to e!cockpit software?

First highly suggest you contact your local WAGO Technical support about e!Cockpit.
Next, your PLC is already e!Cockpit compatible, you juts need to go to the internal WebPages (Access by using https://192.168.2.177) and in the configuration tab you should be able to select the right runtime:

Now for the problem:
CS2.3 is nearly discontinued (I think) and e!Cockpit is also discontinued.

Another way would be to go with the PFC200 SL runtime from codesys and then you can use the codesys 3.5 IDE. (But the runtime is not free).

In any case I think your local WAGO support should be able to give you the best solution for your case.

I donot have option of selection e!RUNTIME.

As far the WAGO support we are the sole distributor of WAGO in Pakistan. What do you suggest we do now?

Dammit I totally forgot the 750-8208 is not supported by e!Cockpit …
Sorry this is my mistake.
I think there is no other way than going back to FW17.