Build errors on Kbus after device duplication (CODESYS 3.5)

CODESYS V3.5 SP19 Patch 2

On a multi-controller project, I copied a complete controller, pasted it in the same project, and renamed the controller along with the IP address for the target.

Since then, I’ve done a ‘Clean All’ and downloaded to one target, but then the build on the other target fails on the Kbus (see image).

I believe it has to do with these Kbus parameters, but have no idea why (it looks exactly the same as any freshly created (from scratch) controllers):

Anyone have any ideas…?

So, apparently performing an “Update Device” solved this issue (even though the version stayed the same). Thanks to Len from Wago Tech Support for that one.

Found this thread as I was experiencing an issue with all K-bus modules being red after a download following a device update. (No compile errors though)

Updated device (PFC200) again, despite being the same version, and with a new download issue was resolved.